View Full Version : Why would my GFi on my spa disconnect trip every time I turn it on?
goss1979
12-16-2008, 03:00 PM
Put a new heater element in the heater tube. I re-connected all the wires and now when I set the breaker it instantly trips!
Owen M
12-16-2008, 04:00 PM
You have a short to ground. Period. probably wired it backwards
Tincan Navy
12-16-2008, 05:30 PM
Ground problem, or something is getting wet.
Rich Z
12-16-2008, 07:10 PM
That GFCI is there to protect you against voltage going to ground through a short or a poorly insulated or damp wire. It is trying to keep you from killing yourself. Go back and recheck the wiring carefully, looking for incorrect connections or poorly insulated joints or frayed wires or strands sticking out.
httnmrtt
12-16-2008, 08:40 PM
Double check your wiring connections and make sure they are correct. It is also possible that you got a bad heater element out of the box. Check it with a continuity meter.
vincent s
12-16-2008, 10:00 PM
if it has a ozonater try to unplug it and try again
78TransAm
12-16-2008, 11:20 PM
There are 3 possibilities:1) You have a ground fault (wire reconnected improperly, shorted to ground or ground missing)2) The new heater is not identical to the one that you replaced and is pulling more amps than the breaker is rated for (a GFI breaker is STILL a breaker)3) The breaker is possibly faulty. GFI breakers are not as "robust" as "plain old breakers". In time, they have a tendency to trip easier.On a high note, the GFI breaker is there to protect you. It is doing it's job. Whatever you do, find and correct the problem BEFORE using your spa. Hope this helps!